How often should fire doors be inspected in a block of flats in England?
I manage a residential block in England with several flats and communal stairwells. The top storey is over 11 metres high. How often do I have to check the fire doors, and does that include the doors to individual flats? I also want to know what applies if a block is lower than 11 metres.
1 Reply
Oldest firstAccepted answer
In England, if your block has two or more sets of domestic premises and is over 11 metres high, you must check communal fire doors at least every 3 months, and use best endeavours to check flat entrance doors at least every 12 months [1][2].
Over 11 metres
- Communal fire doors: checks at least every 3 months. This includes making sure the self-closing devices work [2].
- Flat entrance doors: checks at least every 12 months, on a best endeavours basis. The checks must also include the self-closing devices [2].
- Records: you must record the steps you took for flat entrance doors. If a resident did not grant access, record what you did to try to gain access, such as letters asking for permission [1][2].
What a check involves
The minimum is an inspection for obvious damage or problems. The government says you should not normally need a specialist, and the responsible person should be able to do the checks themselves [1]. Look at:
- any alterations or damage to glazing or air transfer grilles
- gaps around the frame, and whether seals and hinges are fitted correctly
- whether the door closes properly all the way round the frame
- visible damage to the door or the door closer [1]
If you find damage, more detailed checks may be appropriate, and that could involve a specialist [1].
Residents' information
For any building with two or more homes and shared escape routes, you must give residents fire door information to new residents when they move in and to all residents every 12 months [2].
Buildings under 11 metres
The fixed 3 month and 12 month checks do not apply. The general duty to put in place fire precautions under the Fire Safety Order still applies [1]. The materials do not set a check frequency for these buildings. Your fire risk assessment should set it, so ask your fire risk assessor.
Get a competent fire risk assessor or fire door specialist in if you find damage, suspect a flat door has been swapped for a non-fire-rated one, or are unsure how often your building needs checks.
Sources [1] GOV.UK fact sheet: fire doors (regulation 10) [2] Fire Safety (England) Regulations 2022
Applies to England. Written by INFIRISK Editorial from the sources below and checked before posting.