Watermist or sprinklers for a block of flats in England?
I manage a block of flats in England and we are looking at fire suppression. Some suppliers offer sprinklers and others offer watermist. I want to know what Approved Document B actually requires and whether watermist is accepted. What should decide which system we choose?
1 Reply
Oldest firstAccepted answer
Approved Document B asks for a sprinkler system in blocks of flats in England with a top storey more than 11m above ground level, and the materials supplied do not say that watermist can be used instead. [1] The 2020 amendments lowered the trigger height from 30m to 11m. [1]
What the guidance says
- Sprinklers should be fitted throughout the building in accordance with Appendix E. [1]
- They should be provided within the individual flats. They do not need to be in common areas such as stairs, corridors or landings when these are fire sterile. [1]
- For residential buildings, Appendix E points to BS 9251 for design and installation. [2]
- Having a sprinkler system can also change the fire resistance periods allowed for taller blocks. [1]
Where watermist appears
Older government guidance on purpose-built blocks of flats says watermist systems are now available. [3] It names a sprinkler or water mist system as part of one escape option within a flat, with detection in the circulation spaces. [3] That guide also lists a British Standards Institution code of practice for residential and domestic water mist systems. [3] That older guide does not settle whether watermist meets the Approved Document B sprinkler recommendation for new tall blocks. Ask the building control body or a fire engineer to confirm.
What decides between systems
- Whether your building is above the 11m trigger, or is being built, altered or retrofitted.
- Whether the proposed system can be shown to meet Appendix E and the standard it refers to. [2]
- Practicalities of installation and later maintenance. [3]
For existing blocks, the older guidance says retrofitting sprinklers or water mist is unlikely to be reasonably practicable. It does not rule it out where there is clear justification. [3]
Get a fire risk assessor or fire engineer, and your building control body, involved before choosing a system.
Sources [1] Approved Document B (fire safety) volume 1: Dwellings, 2019 edition incorporating amendments [2] Approved Document B (fire safety) volume 2: Buildings other than dwellings, 2019 edition incorporating amendments [3] GOV.UK: Fire safety in purpose-built blocks of flats
Applies to England. Written by INFIRISK Editorial from the sources below and checked before posting.