How often should emergency lighting be tested in a workplace in England?

Solved
1 reply·0 views·Started 11 Nov·Last reply 11 Nov
IE
INFIRISK EditorialINFIRISK Editorial
11 Nov

I manage a small office building in England and I am not sure how often we need to test the emergency lighting. Do we just do a quick check each month, or is there a longer test as well? I also want to know who can do the testing and what we should write down.

1 Reply

Oldest first
IE
INFIRISK Editorial11 Nov

Accepted answer

In England, the government guidance for offices and shops says emergency lighting should have a monthly function test and an annual test by a competent person. Both are part of the usual regime for the responsible person under the Fire Safety Order [2][3].

Monthly test. Operate the test facility long enough to check that each emergency lamp lights. Do this at a time when the lights will not be needed straight after, because the batteries need to recharge. The guidance also mentions a daily visual check of any central controls [2]. Test method varies by system. Many existing systems are tested by hand, often with a "fishtail" key in a special switch. Some modern systems test themselves [2].

Annual test. The guidance says emergency lighting should be tested and maintained by a competent person once a year [2]. After a full discharge test, batteries typically take 24 hours to recharge. The premises should not be reoccupied until the system is fully working, unless alternative arrangements are in place [2]. The guidance points to BS 5266-8 for more detail [2]. The extracts I have do not spell out the annual test duration, so check the standard or ask your competent person.

Who can do it. The monthly check can be done in line with the manufacturer's or supplier's instructions [2]. If you are unsure how to test, contact your supplier or another competent person [2]. Any new work or changes to the system should be done by a competent person to the appropriate standards (BS 5266-1 and BS 5266-8) [2].

Log book. Keep records in a set place on the premises. They should cover testing and maintenance of emergency lighting, and it helps to note who carried out each test and their competence [2].

The responsible person can be a facilities manager or managing agent with control of the premises [1]. You could be fined or face prison for not following fire safety regulations [1].

If you are unsure how to test your system, or your lights fail a test, bring in a competent fire safety or electrical professional.

Sources [1] GOV.UK: fire safety in the workplace [2] GOV.UK: fire safety risk assessment, offices and shops [3] GOV.UK: fire safety law and guidance documents for business

Applies to England. Written by INFIRISK Editorial from the sources below and checked before posting.